It become a little bit fun.... Byte 194 is Outdoor heat exchanger middle temperature .... But only when Byte 199 is greather then 0x03 ( so when extra query exist) , otherwise is a part of power generation... |
Beta Was this translation helpful? Give feedback.
1 reply
-
And Byte 193 is Zone 2 pump speed [rpm] - Convert to DEC (X-1) X 50 |
Beta Was this translation helpful? Give feedback.
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
In Servicecloud i can see new positions:
Also not sure ,if we have already this:
-SHP control [ 1:Disable 2:Enable]
-SHP flow control( forbid deltaT)[ 1:Disable 2:Enable]
Maybe somone have new HP with this features , and can pass a log ?
EDIT:
Byte 10:
7th & 8th bit = SHP Control b01 - Disable b10 - Enable
5th & 6th bit = SHP Flow control( forbid ΔT) b01- Disable b10 - Enable
Byte 115:
1st & 2nd bit = DHW Circulation b01 - off b10 - on
Byte 121:
1st & 2nd bit = Electrical Anode : b01 - off b10 - on b11 - Error
For DHW Circulation and Electrical Anode something have to be also turn on ( with i can't reproduce) , when Service cloud start to show this values... ( something other then only byte 199)
Beta Was this translation helpful? Give feedback.