WAR is disabled instantly #152
Replies: 4 comments
-
Hi, The answer is in your log. Your heatpump is setup using the compensation curve. You have set 2 outside temperatures and gave 2 corresponding water temperatures. This you have done in the wall-mounted controller. The node-red function WAR, is actually exacly the same as the Panasonic native 'Compensation Curve'. Only difference is that the panasonic native implementation is fixed to the outside temperature of the unit (or the external outside temp sensor), where the node red 'WAR-function' is able to use ANY input signal/sensor for this. But.. You can not use both at the same time. That is futile and illogical. :) So... |
Beta Was this translation helpful? Give feedback.
-
AND. IN case you want to keep using the Panasonic Compensation Curve (which is fine), make sure the node red WAR function is set up and containing the same 4 temperatures in the wall-mounted controller. The top two specifically the last two (-6 / 30 ) are less important. Make sure the line looks nice. |
Beta Was this translation helpful? Give feedback.
-
Hi Ed |
Beta Was this translation helpful? Give feedback.
-
You can change the Compensation curve as well remotely. Use the EXPORT button in the WAR-function tab. :) That way you send 4 new temperatures. Just to note: The biggest advantage of the NR-WAR function (where I use it for) is that you can use any sensor. |
Beta Was this translation helpful? Give feedback.
-
When I activate WAR, it is active for a second and then automatically disabled. The log says:
08/01 17:39:46 - Function - WAR: 0
08/01 17:39:45 - Function - WAR: 1
08/01 17:38:42 - Function - WAR: 0
08/01 17:38:41 - Function - WAR: 1
08/01 17:34:29 - Function - WAR: 0
08/01 17:34:29 - Function WAR: Compensation curve active. Using internal Panasonic WAR function. NodeRed WAR function is now disabled
08/01 17:34:28 - Function - WAR: 1
Why is this and what can I do to use WAR
Thanks Uwe
Beta Was this translation helpful? Give feedback.