Think carefully about your inputs. You are supplying 200 m3/s of ambient air at ambient temperature and removing 200 m3/s of hot air. Are these mass flows equal? |
Beta Was this translation helpful? Give feedback.
0 replies
-
It is true that the density should increase with this setup. Given that the fire ramp up instantaneously at the start of the simulation, when the temperature in the duct is almost steady at the later phase of the simulation, it is expected that the density and mass flow are steady too. However, the density and mass flow are still increasing. |
Beta Was this translation helpful? Give feedback.
5 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
The model is shown in the image below and contains two spaces, i.e. one 'smoke generation space' (at the bottom of the image) and one 'discharge space' (on the top of the image). The smoke is extracted from the 'smoke generation space' and discharged to the 'discharge space' via an HVAC duct in FDS with a constant flowrate (200m3/s). Two makeup vents (100m3/s each) is provided at two sides of the 'smoke generation space'. The four sides and the top of the 'discharge space' are set to open boundaries. The fire is set to ramp its peak quickly from the start of the simulation so as the HVAC duct volume flowrate.
The HVAC duct quantities are logged. It is observed that the duct volume flow and temperature reach steady state quickly after the simulation starts. However, the mass flow and density inside the duct are monotonically increasing. The density is exceeding 2.5kg/m3 at the end of the simulation. It does not seem realistic.
Is it the intended behaviour of an HVAC duct in FDS? Or does it exceed the capacity of an HVAC duct in FDS?
The FDS file is attached.
hvac_setup_test2.txt